LainaaStep 1: If control is generating System Errors such as "Alarm 910 Ram Parity" or "Alarm 911 Ram Parity", control memory must be first initialized. Parity Alarm is
usually caused by low memory backup battery.
Step 2: Initialized/clear memory by press and holding "RESET" & "DELETE" keys simultaneously while powering ON the control.
Step 3: Control should power up to Alarm screen and it should show several alarms including
Alarm 100: Parameter Write enabled (PWE)
417: X Axis Digital Parameters
427: Y Axis (for milling machines) Z Axis (for lathes) etc.
Step 4: Push in E-Stop (Emergency Stop) button. Press "PARAM/DGNOS" key once to go to parameter screen.
Press "Page Down" key to go down to Parameter 38. Set parameter number 38 according to your backup list.
Alarm 000 Power off alarm may generate causing the control to switch to alarm screen. Press "PARAM/DGNOS" to return to paramter screen.
Page down to Parameter number 900 (you can also press "No." key then type in "900" then input to skip to parameter number 900.
Set parameter 900 to approximately about parameter 932 according to the backup list. When certain parameter 900 area data is set, control will generate a
warning message of something to the effect saying: press "Del" (Delete key) or "CAN" (cancel key) to continue. Press "DELETE" key and continue setting
900 series parameters according to the list.
Step 5: Turn power OFF and then back one after about one minute. Control should come on and show alarm screen still with several alarm previously mentioned.
If parameter backup is available on computer, setup the RS232 parameters on the control
Step 6: Input NC parameters as follow:
Select EDIT mode.
Select PARAMETER screen.
Press "INPUT" while holding "EOB" (End of block) key.
*Note: INPUT will flash in the lower right-hand corner and NC parameters will be input.
Alarm 000 Please turn power off message will appear once parameters are loaded. Power OFF/ON.
Step 7: Input PMC Parameters as follow:
Select EDIT mode.
Select DGN screen.
Hold EOB and press INPUT.
Step 8: Input NC Programs as follow:
Select EDIT mode.
Select PROGRAM Memory screen.
Verify Program Protect Key is OFF.
Press INPUT.
Step 9: Input Offsets as follow:
Select EDIT mode.
Select PROGRAM Memory screen.
Verify Memory Protect Key is OFF.
Press INPUT.
Run this program to write data to OFFSET screen.
RS 232 SETTING :
SETTING PAGE Personal Computer Settings
ISO = 1 (0:EIA 1:ISO) 4800 Baudrate
I/O = 0 (0:PORT 0, 1:PORT 1) 2 stop bits
ISO Code (ASCII)
PARAMETERS Even parity
0002 = 1XXXX0X1 Data length = 7 bits
0038 = 1010XXXX Control Codes (Xon/ Xoff used)
0055 = XXXXX000 LF for End Of Block
0070 = 0XXXXXXX
0552 = 10 (Baud rate)