tajuaisko joku mikä on sillä on hätänä?
Diagnostics buffer of the module Unspecific\Upload\MDD_Lifelist-Substitute-S7300-CPU
Order no. / name Component Version
6ES7 315-2AF03-0AB0 Hardware 1
- - - Firmware V 1.2.0
Firmware expansion Firmware expansion 0.0.0
Rack: 0
Slot: 2
1 of 100;
Event ID: 16# 4562
STOP caused by programming error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 100
Module address: 2538
Previous operating mode: RUN
Requested operating mode: STOP (internal)
2/1/2013 23:00:34.209
2 of 100;
Event ID: 16# 253A
DB not loaded
DB number: 42
Requested OB: Programming error OB (OB121)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 23:00:34.209
3 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 23:00:33.121
4 of 100;
Event ID: 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by programming error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
2/1/2013 23:00:33.069
5 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by programming error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 23:00:32.835
6 of 100;
Event ID: 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 2
Number of distributed stations: 4
2/1/2013 23:00:21.528
7 of 100;
Event ID: 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
2/1/2013 22:59:57.671
8 of 100;
Event ID: 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
2/1/2013 22:57:41.110
9 of 100;
Event ID: 16# 4562
STOP caused by programming error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 100
Module address: 2538
Previous operating mode: RUN
Requested operating mode: STOP (internal)
2/1/2013 22:56:35.142
10 of 100;
Event ID: 16# 253A
DB not loaded
DB number: 42
Requested OB: Programming error OB (OB121)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 22:56:35.142
11 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 22:56:34.104
12 of 100;
Event ID: 16# 1382
Request for automatic warm restart
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
2/1/2013 22:56:34.052
13 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 22:56:33.826
14 of 100;
Event ID: 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 2
Number of distributed stations: 4
2/1/2013 22:56:22.523
15 of 100;
Event ID: 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
2/1/2013 22:55:58.671
16 of 100;
Event ID: 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
2/1/2013 22:55:49.365
17 of 100;
Event ID: 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
2/1/2013 22:53:49.783
18 of 100;
Event ID: 16# 4307
Memory reset started by PG operation
Previous operating mode: STOP (internal)
Requested operating mode: STOP (memory reset)
2/1/2013 22:53:49.116
19 of 100;
Event ID: 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
2/1/2013 22:53:48.033
20 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 22:22:46.196
21 of 100;
Event ID: 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 22:22:46.195
22 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 22:22:46.102
23 of 100;
Event ID: 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
2/1/2013 22:22:43.671
24 of 100;
Event ID: 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
2/1/2013 22:22:34.318
25 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 22:12:30.196
26 of 100;
Event ID: 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 22:12:30.195
27 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 22:12:30.102
28 of 100;
Event ID: 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
2/1/2013 22:12:27.671
29 of 100;
Event ID: 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
2/1/2013 22:12:20.183
30 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 22:11:14.196
31 of 100;
Event ID: 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 22:11:14.195
32 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 22:11:14.102
33 of 100;
Event ID: 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
2/1/2013 22:11:11.671
34 of 100;
Event ID: 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
2/1/2013 22:11:04.356
35 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 22:10:48.196
36 of 100;
Event ID: 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 22:10:48.195
37 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 22:10:48.102
38 of 100;
Event ID: 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
2/1/2013 22:10:45.671
39 of 100;
Event ID: 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
2/1/2013 22:10:38.521
40 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 22:09:42.196
41 of 100;
Event ID: 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 22:09:42.195
42 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 22:09:42.102
43 of 100;
Event ID: 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
2/1/2013 22:09:39.671
44 of 100;
Event ID: 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
2/1/2013 22:09:32.300
45 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 22:08:35.196
46 of 100;
Event ID: 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 22:08:35.195
47 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 22:08:35.102
48 of 100;
Event ID: 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
2/1/2013 22:08:32.671
49 of 100;
Event ID: 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
2/1/2013 22:07:53.592
50 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 22:06:57.196
51 of 100;
Event ID: 16# 1382
Request for automatic warm restart
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 22:06:57.195
52 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 22:06:57.102
53 of 100;
Event ID: 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
2/1/2013 22:06:54.671
54 of 100;
Event ID: 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
2/1/2013 22:06:26.646
55 of 100;
Event ID: 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
2/1/2013 21:59:11.844
56 of 100;
Event ID: 16# 4307
Memory reset started by PG operation
Previous operating mode: STOP (internal)
Requested operating mode: STOP (memory reset)
2/1/2013 21:59:11.157
57 of 100;
Event ID: 16# 4562
STOP caused by programming error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 100
Module address: 2538
Previous operating mode: RUN
Requested operating mode: STOP (internal)
2/1/2013 21:56:03.204
58 of 100;
Event ID: 16# 253A
DB not loaded
DB number: 42
Requested OB: Programming error OB (OB121)
OB not found, or disabled, or cannot be started in the in the current operating mode
2/1/2013 21:56:03.204
59 of 100;
Event ID: 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
2/1/2013 21:56:02.130
60 of 100;
Event ID: 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by programming error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
2/1/2013 21:56:02.078
61 of 100;
Event ID: 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by programming error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
2/1/2013 21:56:01.842
62 of 100;
Event ID: 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 2
Number of distributed stations: 4
2/1/2013 21:55:50.536
Inhoan Siemenssiä yli kaiken, enkä siitä paljon mitään ymmärrä. Mutta kuitenkin tuo herja ettei DB42 löydy. Onko logiikassa DB42 olemassa? Voisi kuvitella että FC100 yrittää hakea jotain tietoa DB42:sta, mutta ei löydä sitä.
ei näkynyt DB42:sta
tämä ongelma on sorvissa josta oli kuljetuksen aikana patteri tyhjentynyt ja piti ladata backup että sai päälle koneen.
koneessa jää käynnistys näitten takia vaiheeseen..
voisko olla että backuppi jotenki virheellinen?